    How far back should a separate insulated bonding conductor be isolated from all other bonding conductors?

  2. #2
    Inactive Member CRM's Avatar
    Join Date
    February 29th, 2004
    Posts
    32
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    If you are refering to isolated ground receptacles, the ground should be run back to the main service ground, the point at which the neutral and equipment ground are bonded together, and where the main ground electrode is terminated to.